ad a extra 240v socket

Sep 5, 2008
2
0
0
we have a 1995 ace diplomat and would like to change the single sockets from single to double(there are 2 single sockets) is this possible?????
 
G

Guest

I would think no problem, however, do watch the loading you are putting on the system. If you try to run 2 items at 3 kilowatts each at the same time you may have a problem. Also have a quick check of the rating in your MCB box, this is usually around 25 amps.

As the van is aged 1995 you may also want to check the wiring is still in good shape.
 
Jul 15, 2008
3,911
1,097
20,935
Click on Towsure link to the left of your post on Practical Caravan page.

Put in E665 into search.

Then do another fo E670

Bear in mind what Scotch Lad says.
 
Nov 6, 2005
9,176
3,640
30,935
MCB at 25 amps ??? The hook-up cable is only rated for 16 amps.

Our 2001 Bailey has two MCBs, 5 and 10 amp, with the circuits distributed appropriately between them.
 