KeefySher said:I use the rule of thumb of 220 / Amps to give me the Watts.
I hope that's a typo and you mean 220 x Amps, not 220 divided by Amps.
Here's the sticky out tongue thingy
KeefySher said:I use the rule of thumb of 220 / Amps to give me the Watts.
JamesH said:Hi Prof.
It was the caravan mcb that tripped out. It wasn't overloaded in the van as we always switch the immersion and/or convector heater off when the elec kettle is on. It was then that I plugged in the voltage indicator, noticed that the supply voltage was very low and assumed that was the reason for it tripping out.
I was working on the assumption that if the supply V was 240V and the appliances were drawing 2400W then that would equal 10A but if the supply voltage was only 215V then that would equal 11A.
When we were away last week the supply voltage occasionally dropped below 215V momently.
One thing that happened that I can't understand is that whilst on site the state of battery charge dial only just managed to stay in the green (with no 12v appliances connected) but on arriving home and connecting to the mains after a couple of hours or so it was showing maximum charge
WoodlandsCamper said:KeefySher said:I use the rule of thumb of 220 / Amps to give me the Watts.
I hope that's a typo and you mean 220 x Amps, not 220 divided by Amps.
Here's the sticky out tongue thingy
WoodlandsCamper said:Are you by any chance using an ipad or similar? Icons are OK using a desktop PC.
Edit - I don't think I've ever had auto-correct, but spelling mistakes are still notified by the wavy red line underscore.
saint-spoon said:So what happens if there is a constant load attached to the electric motor that is being supplied by the voltage? (not that you will get this situation in a caravan).
Just covering all bases.ProfJohnL said:saint-spoon said:So what happens if there is a constant load attached to the electric motor that is being supplied by the voltage? (not that you will get this situation in a caravan).
That is not relevant to this thread.
Abinitio1989 said:Quite - requiring use of long cables is a serious deign flaw
GStockton said:Just a couple of facts from BS 7671 amd3
1 reg 708.530.3 states caravan pitch shall not be more than 20 m from the supply pillar
2 reg 721.55.2.6 States a flexible cable of continuous length of 25m + or - 2m shall be used. For 16 amps a minimum of 2.5mm.
So if you need to use more than 25m of lead,then the caravan site you are on does not comply with the relivent British Standards go and ask them who did there last Electrical Installation condition report..
GStockton said:Just a couple of facts from BS 7671 amd3
1 reg 708.530.3 states caravan pitch shall not be more than 20 m from the supply pillar
2 reg 721.55.2.6 States a flexible cable of continuous length of 25m + or - 2m shall be used. For 16 amps a minimum of 2.5mm.
So if you need to use more than 25m of lead,then the caravan site you are on does not comply with the relivent British Standards go and ask them who did there last Electrical Installation condition report..
ProfJohnL said:This issue of cable length needs to be put into perspective. Every length of cable that is carrying current will produce a Voltage drop. IF you use a longer cable for teh same current you will experience a bigger voltage drop, But in reality we are talking about and 25M EHU add ing 0.72 of an Ohm to the system resistance. If you were pulling the full 16A that would only equate to an 11.5 volt drop, but the voltage drop is proportional to teh current draw, so if you were only pulling 4A the volt drop on teh EHU cable would be 2.9V
Don't forget that there will be inherent resistance in all the sites wiring, and how long is that?
In reality the voltage drop caused by an EHU cable should not by it's self compromise the operation of a caravan.