To Gary and all.
I believe there are some misconceptions being aired in this thread and Steve's original question is not being addressed safely.
Back to fundamentals, for an electric current to flow and operate an appliance, there has to be a circuit made from the power supply and back again. This only requires two wires, and in UK terms this is Live and Neutral. The third wire in the UK is a safety device commonly known as the "Earth" but its correct name is a 'Continuous Protective Conductor'
The CPC connects all exposed metal parts of appliances to the earthing point of the supply. Manufactures have to go to considerable lengths to ensure that the CPC is correctly installed and it has to offer a very low resistance path from any exposed conductive surface back to the earth point.
Under correct operating conditions, there should be no contact what so ever between either the Live or Neutral circuits and the CPC. If a contact is made there is a fault, and the fact that the CPC provides an easy path back to earth means that you should not receive a shock, as the current will preferentially flow in the CPC rather than you.
Now if Steve is receiving a shock, it means that his caravan is not properly earthed. That is a fault. It could be in his caravan, or in the site supply. An electrician should be able to establish where the fault lies by testing.
If he always receives a shock whichever site he is on, then it points to a fault in his caravan, but if the shock is site specific, then it points to the site wiring.
Steve's shock is indicative of a wiring fault, and somewhere either in the caravan or the site an appliance has developed a fault to allow current into the CPC circuit. The polarity of the supply is not relevant to this, but it is a separate safety issue
With modern caravans and the equipment supplied, the polarity of the supply should not affect the safety of the CPC. Polarity is important to ensure that on /off single pole switches will disconnect the Live conductor to safely turn off appliances. Some appliances now use double pole switches which are the safest approach because they isolate both Live and Neutral, but not the CPC.
Steve get you caravan checked by an electrician. If he shows no fault with the van for other peoples safety contact the site where you got your shock and report it as a safety issue.