If the main fuse is 100A supplying 20 caravans on 16A supplies
and each is pulling 10A - well within the post/cable limit, the current is 200A - bang goes the fuse. At home if you add up the value of all the circuit breakers in the consumer unit, they will always be greater than the main supply fuse of 60A or 100A.
Kettles are not likely to be such a problem as they are a short term, intermittent load and it is very unlikely that all 20 caravans boil a kettle at the same time but a 2KW heater pulls 9A, early, cold morning as everyone is getting up there is a high possibility of all heaters being on, 20 x 9 = 180A
and each is pulling 10A - well within the post/cable limit, the current is 200A - bang goes the fuse. At home if you add up the value of all the circuit breakers in the consumer unit, they will always be greater than the main supply fuse of 60A or 100A.
Kettles are not likely to be such a problem as they are a short term, intermittent load and it is very unlikely that all 20 caravans boil a kettle at the same time but a 2KW heater pulls 9A, early, cold morning as everyone is getting up there is a high possibility of all heaters being on, 20 x 9 = 180A