As far as I know the power limiter incorporated into the Alde heating system only monitors the power the heating appliance uses. It does not take into account any other appliance that might be drawing power from the mains.
Thus the amounts power the fridge or any other non Alde heater related appliance should makes no difference to the Alde power limiters operation.
Even if a fridge mains element does draw 170W (0.74A at 230Vac) )will not change the Alde's power draw.
Not quite!
If that's all it does it's been incorrectly fitted and would serve no useful purpose at all.
It should be fitted in the main power intake and then it monitors the total use by the van.
If the monitor unit is set at 6 amps and the alde is on 2kw it will reduce the alde to 1kw thus staying below the 6amp total load.
If I turn the kettle on with the heating running it switches the heating off until the kettle has finished. It's just a current sensing coil the clever bit is already in the software of the 3020.
I have fitted one to my van as an extra and it works well and saves us having to remember when on low current EHU to switch the heating off when we need to use other 1kw items.
Used to limit power consumption of the vehicle. Reduces the output of the electric element in stages if the load is too high. This prevents the circui...