There are a lot of ifs and buts but looking purely from an efficiency perspective Its possible to be precise about this matter:-
Firstly it us unfair to make direct comparisons between a touring caravan and a domestic building in terms of thermal mass, and insulation. They are very different especially as the thermal mass of a caravan is much much less than a typical room in a house.
The small thermal mass in the caravan allows it to respond quickly to a heat input, both the air and the fabric warm almost equally together. Put the same heater into a domestic room, and whilst the air may heat up the fabric lags a long way behind.
For the set up I reported on earlier as 3kW heater took about an hour to raise the internal temperature to 25C above ambient (-5 to +20C) When it reached 20C, the heaters thermostat started to modulate the flame size to maintain 20C. Using some fairly exotic gear it was established that to maintain that temperature the heater was turning down to about 1kW (from 3kW)
Armed with that information it is possible to say that if the caravan was maintained at 20C for 10 Hours over night it would use 10 x 10kW or fuel.
If the heater was turned off over night and the caravan allowed to cool for 9 hours then it was turned on full for the tenth hour it would use only 3kWh - a saving of 7kWh.
The above ignores any argument for convenience or comfort or reducing heat input for a lower temperature, but if we were to assume the heat input rate fell to only 500W for 10 hours that still 5kWh and still more gas used compared to turning the heater of completely.
On purely efficiency grounds turning off over night is better than just turning it down BUT if you are also considering comfort and convenience then the extra cost of burning the heater over night might been seen as good value - that is a personal choice.
Firstly it us unfair to make direct comparisons between a touring caravan and a domestic building in terms of thermal mass, and insulation. They are very different especially as the thermal mass of a caravan is much much less than a typical room in a house.
The small thermal mass in the caravan allows it to respond quickly to a heat input, both the air and the fabric warm almost equally together. Put the same heater into a domestic room, and whilst the air may heat up the fabric lags a long way behind.
For the set up I reported on earlier as 3kW heater took about an hour to raise the internal temperature to 25C above ambient (-5 to +20C) When it reached 20C, the heaters thermostat started to modulate the flame size to maintain 20C. Using some fairly exotic gear it was established that to maintain that temperature the heater was turning down to about 1kW (from 3kW)
Armed with that information it is possible to say that if the caravan was maintained at 20C for 10 Hours over night it would use 10 x 10kW or fuel.
If the heater was turned off over night and the caravan allowed to cool for 9 hours then it was turned on full for the tenth hour it would use only 3kWh - a saving of 7kWh.
The above ignores any argument for convenience or comfort or reducing heat input for a lower temperature, but if we were to assume the heat input rate fell to only 500W for 10 hours that still 5kWh and still more gas used compared to turning the heater of completely.
On purely efficiency grounds turning off over night is better than just turning it down BUT if you are also considering comfort and convenience then the extra cost of burning the heater over night might been seen as good value - that is a personal choice.