Apart from Hugh and myself, everyone else is simply stabbing in the dark over this issue.
I am the engineer who services Hughs van each year and until this year there has never been a problem with the harmonics in the regulator.
This year for some inexplicable reason it (the regulator) decided to make a humming noise only when the cooker was in operation, at all other times and with all other gas equipment ON, no noise.
As soon as any of the hob burners were lit, or the grill or th eoven, in any combination or alone, the humming started.
Suspecting a possible internal fault with the regulator, I changed it for a new one, and it still did exactly the same.
I then tried a single stage regulator, and it behaved in exactly the same manner.
Back to original regulator, fully checked for oil contamination,,,none.
Fully checked for input pressure and output pressure,,,,nothing wrong at all, eveything exactly as it should be.
Pigtail checked for oil contamination,none.
System fully pressure tested, absolutely no leaks and all as it should be.
The only conclusion I can come to, having had no feedback from the sources I have asked about the problem, is that it must be something to do with pipe routing to the cooker, or the amount of gas being drawn into the cooker settting up a vibration.
Hugh, having done what he has done, has found a way of overcoming it, something I will admit never crossed my mind at the time to try, however it has not got rid of the harmonics as such,but at least it has stopped the very annoying drumming noise.
There is absolutely nothing wrong with the current regulator, pigtail or appliances, all having been checked and a flue gas analysis carried out on each appliance to ensure they are all burning correctly.
We all learn new things every day, and this is one of those learning curves which may well come in useful in the future.