Polarity Tester...How do you use it ??

Mar 14, 2005
78
0
0
Visit site
Hi,

I've just purchased a polarity tester ready for our summer hols,

but I'm not sure under what cicumstances I'd need to use the polarity reverser I've also made.

Having connected to the mains ( in Holland ) and plugging in the polarity tester, it will read either;

Live Neutral Reverse

No Earth

Neutral Fault

Live Earth Reverse

Correct

Which of the above results would require me to use the polarity reverser ?

Any help or advice would be welcome.

Thanks,

Mike.
 
Nov 4, 2004
1,191
0
0
Visit site
Hi

I take it you have the plug in neon light type?

If so the neons light to show the state of the electrics entering the van,depending on what neons are lit will show what you need to change in your electrical lead.ie live neutral reverse will mean you swap the live and neutral wires around in the plug.

Please be careful i must admit the only one i have seen abroad is neutral and earth swapped.

Best thing to do is buy the connector cables and change before you go to save time when you arrive plus you know they are tested and correct.

I carry 3 types:The 2 pin to commando(blue plug) 2 of these one earth neutral swapped and 1 commando to commando eath neutral swapped.
 
Jul 15, 2005
2,175
1
0
Visit site
Mikey,

I sincerely hope your reversal lead is not as you say - switching earth and neutral is deadly.

If you need to correct polarity - you need to swap line and neutral - the earth is always connected to earth.

Please check - I'm hoping it was just a typo in your posting

Mike,

Polarity reversal:

In the UK, only the live wire is switched by household and caravan MCB and RCD trips - leaving the neutral wire permanently connected to the inside of any appliance.

In Europe both the live and the neutral wires are switched by their modern MCB and RCD trips. And since polarity doesn't matter for the correct operation of the AC mains appliance, power sockets are randomly wired for live and neutral - indeed in Holland and Germany - the Schuko plug can itself be inserted in the wall socket either way up - it truly doesn't matter.

When you take your UK caravan to say, Holland, then roughly 50% of the time the live and neutral wires will be crossed compared to what you expect.

This doesn't affect the safe operation of the appliance, but if there was a fault and the UK caravan MCB trip "flipped off" - then there is roughly a 50% chance that the neutral wire is still carrying power into the heart of the appliance.

And there is then a chance of electrocution if you start fiddling with the internals of an appliance without pulling the plug out of the socket. Don't do this anyway - even in the UK - unless you are a trained engineer

The correct solution to this problem is for UK caravans (and homes) to follow the European dual switching system (and cut both feeds). But in the meantime, you can protect yourself by checking the polarity and (if necessary) insert a polarity reversing cable between the site power and your normal hook-up lead.

In the list of examples you quote - live neutral reverse - is the situation where a polarity reversal lead is used.

You should take the following leads with you:

A - normal UK hook-up lead (with the blue IP44 connectors)

B - a short (1 metre or less) cable with a CEE 7/7 "universal Schuko" plug to blue IP44 socket - most sites in Holland will have the IP44 sockets - but a few (and quite a lot in France) will use an outdoor version of the household Schuko socket.

This cable lets you bridge the gap between Schuko socket and caravan hook up

C - a short (1 metre or less) cable with an IP44 plug to IP44 socket - with the live and neutral wires crossed at one end only - and this is your reversal cable

Then use cables A (and B if necessary) to connect the van to the site power

Then test polarity, and insert cable C if necessary to correct

Easy - and easy for us - we have an Eriba with dual switching so we just forget about this.

Robert
 
Jul 15, 2005
2,175
1
0
Visit site
Mike,

To answer you question about what do the test results mean:

Correct - No problems here

Live Neutral Reverse - use the polarity reversal cable (and check again by the way)

No Earth - disconnect immediately and seek help from the site

Neutral Fault - seek help from the site - nothing will probably work

Live Earth Reverse - disconnect immediately and seek help from the site - but the RCD trips will probably have already cut the power. Avoid touching the body of the caravan before you pull the plug.

Robert
 
Nov 4, 2004
1,191
0
0
Visit site
Hi

I take it you have the plug in neon light type?

If so the neons light to show the state of the electrics entering the van,depending on what neons are lit will show what you need to change in your electrical lead.ie live neutral reverse will mean you swap the live and neutral wires around in the plug.

Please be careful i must admit the only one i have seen abroad is neutral and earth swapped.

Best thing to do is buy the connector cables and change before you go to save time when you arrive plus you know they are tested and correct.

I carry 3 types:The 2 pin to commando(blue plug) 2 of these one earth neutral swapped and 1 commando to commando eath neutral swapped.
Sorry typo

swapped live and neutral over on cables
 
Mar 14, 2005
78
0
0
Visit site
Thank you very much for such comprehensive replies Robert.

You've answered all my questions and educated me a little in the process !!

Thanks again,

Mike.

P.S I bet people love being pitched next to you, particularly if they have any problems !!
 