• We’re currently investigating an issue related to the forum theme and styling that is impacting page layout and visual formatting. The problem has been identified, and we are actively working on a resolution. There is no impact to user data or functionality, this is strictly a front-end display issue. We’ll post an update once the fix has been deployed. Thanks for your patience while we get this sorted.

Spur

Any body changed old type spur on ultraheat to the new c-line fused spur 10 amp first photo show wire to fit on second photo many thanks
 

Attachments

  • IMG_3885.jpeg
    IMG_3885.jpeg
    1.5 MB · Views: 15
  • IMG_0288.png
    IMG_0288.png
    1.2 MB · Views: 16
No, and please remember a standard fused/unfused switch is normally rated at 20A, the C line is only rated at 10A and the ultraheat takes about 8A so if you use the C line its life may be shorter and please if you proceed inspect it regularly. The blue wires go into N1 and N2 , the live wire ( brown) go to 1 and 2
 