Blown Air Heating

Jul 31, 2012
2
0
0
Visit site
Hi
I wonder if any one can help me your thoughts and comments would be much appreciated.
I've just bought a 2008 Bailey Ranger with a truma blown air heating system.
My problem is when I run it on 240v only I only get heat when it's on the 2000 watt setting with the heat setting on 7-10
This as you can imagine makes the van very warm.

Also if I turn it down I we wake up cold as the heating starts to blow cold air through.
Do you have any advice on settings etc?
 
G

Guest

A common problem, the cause though is for one or a combination of reasons, below is my overview of how the Truma Ultra-heat should work and the reasons why not!
(In your case, I'd fully expect the control board and lack of or mis-positioned remote temperature sensor is at fault.)

The Ultraheat’s wattage settings are there so you can make use of low amperage hookups, ideally 500W for 6A, 1000W for 10A and 2000W for 16A hookups, their not there to adjust the temperature of the van.
(You could of course use 6A for 1000W and 10A for 2000W, however you will be very limited on what else you can use at the same time, remembering to switch down or off while boiling a kettle can help get the best use out of low amperage hook up’s)
The Ultraheat is thermostatically controlled, therefore the wattage used will simply mean the fire is heating for shorter or longer periods. Where the problems arise then is if the temperature control is not working correctly, this is often due to the heat from the elements directly affecting the sensor itself,. The sensor is within the control switch, depending then where the switch is installed, this means the heat of the fire can bring the temperature sensor up to that set on the dial directly and the elements switch off, you and the van are still cold but the sensors toasty and takes forever to cool before switching the fire back on!!
A few common bad places to find the switch are in the side of the wardrobe above the fire or in a bed box where blown air pipes run, or perhaps even behind where the TV sits so the heat from the back of the TV or it’s transformer warms it up!
Due to this and particularly overnight, it's become something of an urban myth to set it at 500w or 1000w, this or that number on the dial and fan speed setting. In truth what's happening is the available heat is not capable of reaching the set temperature so never switches off, it's a useful work around but not how it should work.
The real solution is to fit a ‘remote’ temperature sensor and attach it to the gas fires sensor, if a remote is already fitted, it to will usually react better if moved to this location.

Setting the fan on manual speed means the fan runs at this speed regardless of the amount of heat being produced, I would suggest manual fan is only for use without heat for cooling in summer, if infact it has a use?!
Setting the fan to ‘A’utomatic allows the heat produced to control the fan speed ‘up’ to the speed set on the dial, you can then, keep this set maximum low and therefore quiet, overnight perhaps?
Automatic means the fan will run slowly initially and speed up as the air passing through gets warmer, doing it this way allows heat and fan to be switched on together and doing away with waiting xx minutes as often suggested.
I would suggest as a start and during the day, the wattage selected is as high as the hook up allows and then fan speed set to maximum on Automatic.
This provides the maximum heat if required and the fans speed will respond to change in temperature, ie, fast when heat cycle is on and slow when heat is off.
After that you can fine tune to suit your own needs

Other heating problems concern the control board, the elements are switched on and off by relays and the contacts burn out, particularly the two 1kw relays. If this happens you may think you have it set to 2kw but only one element is working, finally perhaps leaving you with just 500w working when both 2kw and1kw settings no longer work.
(Note, relays will still be heard to ‘click’ but unless you have heat, their not working)
The 12v for control also comes from this board and the transformer sometimes packs up, apart from no heat, you will lose the green light in the switch if this happens
Also if no heat is forth coming, there are two safety thermostats which switch the power to the elements off if things to hot. The lower one set at 125C will automatically reset after cooling, the higher 175C stat will hold itself off until power is removed, you must then switch off the mains supply to the heater and then it will reset automatically after a few minutes when power can be restored.
The lower 125C stat can fail when hot but well before it’s set temperature, this will mimic a relay fault and the heating switch off before the set temperature on the dial is reached. However checking the stat for continuity when cold will show a perfect reading, only way to be sure is to change it.

Note; if either thermostat is faulty it won't be able to reset, if faulty it can sometimes show itself by the vans main RCD tripping, but not always.

Finally, the mains isolation ‘fused switch spur’ can loose it’s connection through the built in fuse, the fuse is not the problem but the fuse holders connections that seem to be the problem

The main control switch itself seems generally reliable but the odd one does fail, the fan control switch when set to ‘A’ should make a positive connection and not switch on and off at the merest touch.

The numbers on the dial represent roughly 4degs and 9 is 32degs or thereabouts, this in theory makes 6 or 7 'normal' but it's what feels comfortable that matters not the number.

Other problems not caused by the heater itself are long runs of un-insulated blown air pipe running outside under the floor, insulating this will improve matters considerable.
The kitchen cabinet is often fitted over a wheel arch, much larger than required holes for clearance over the arch are used, the resultant heavy draught coming from behind the fridge can be eliminated by simply sealing the gap on the fridge side of the centre
cupboard.
Any draughts coming from the front of the fridge should also be eliminated.
Fix bed models very often have large floor vents under the bed, these are only useful in storgage and are easily block with a towel while the vans in use,

It’s also known for blown air outlets to blow toward the fire and this will upset the temperature control, adjusting these to blow away or even blocking off completely can actually improve overall heating.

Everything installed and working as it should, there is no good reason why the electric heating should not work very well and keep an even temperature to suit your needs.

However, it must be remembered the van needs to be warmed through thoroughly, (not just the air), before the heating is turned down. While the vans cold it will constantly drag heat from the air and this in turn needs constant topping up or the van will always feel ‘draughty’. It's most useful then while particularly cold to use gas as well for the first couple of hours, also, if the heating is off during the day to turn it back on at the first sign of a chill.
 

JRG

Aug 17, 2012
1
0
0
Visit site
I have just turned on the Truman heater in our caravan to run on electric hook up as on site however it doesn't seem to be working, turned it on to gas and no problem?

Any ideas?
 
G

Guest

A few more possibles above but the first is, is the green light in the switch on?

If not, maybe it just the mains isolation switch that has been turned off?!
 
Sep 30, 2021
4
0
10
Visit site
A few more possibles above but the first is, is the green light in the switch on?

If not, maybe it just the mains isolation switch that has been turned off?!

my heater has just stopped working. Was working great last night. Now it’s producing no heat.
Where is the green light? I have a Burstner only just brought it and not familiar with caravans.
Thanks
 
Nov 11, 2009
20,009
6,080
50,935
Visit site
my heater has just stopped working. Was working great last night. Now it’s producing no heat.
Where is the green light? I have a Burstner only just brought it and not familiar with caravans.
Thanks
It’s normally a very small light in the rotary control switch used to set the power level and room temperature. If you have a picture I could mark it up for you.
 
Mar 14, 2005
17,528
3,029
50,935
Visit site
As with any mains electrical or gas appliance if a problem or fault arises, and you need to ask "how to fix it" then its most likely you are not competent to try fixing it. It is most sensible to seek help from a professional. In some cases it is a legal requirement.
 
  • Like
Reactions: RogerL and DaveA1

Mel

Mar 17, 2007
5,325
1,266
25,935
Visit site
As with any mains electrical or gas appliance if a problem or fault arises, and you need to ask "how to fix it" then its most likely you are not competent to try fixing it. It is most sensible to seek help from a professional. In some cases it is a legal requirement.

Completely agree Prof. However when you are new to Caravanning there may be a simple thing that you have overlooked such as removing the external vent cover from older gas heaters or filling the tank with water. Always worth asking just in case, but beyond that, call in the professionals.
Mel
 

Mel

Mar 17, 2007
5,325
1,266
25,935
Visit site
We had a problem with our Whale blown air heater. One minute working the next not. Then randomly working again. Turned out it was the rotary switch. Wasn’t making contact when you turned it. We didn’t fix it. Servicing people did.
Mel
 
Aug 26, 2011
7
2
18,515
Visit site
A common problem, the cause though is for one or a combination of reasons, below is my overview of how the Truma Ultra-heat should work and the reasons why not!
(In your case, I'd fully expect the control board and lack of or mis-positioned remote temperature sensor is at fault.)

The Ultraheat’s wattage settings are there so you can make use of low amperage hookups, ideally 500W for 6A, 1000W for 10A and 2000W for 16A hookups, their not there to adjust the temperature of the van.
(You could of course use 6A for 1000W and 10A for 2000W, however you will be very limited on what else you can use at the same time, remembering to switch down or off while boiling a kettle can help get the best use out of low amperage hook up’s)
The Ultraheat is thermostatically controlled, therefore the wattage used will simply mean the fire is heating for shorter or longer periods. Where the problems arise then is if the temperature control is not working correctly, this is often due to the heat from the elements directly affecting the sensor itself,. The sensor is within the control switch, depending then where the switch is installed, this means the heat of the fire can bring the temperature sensor up to that set on the dial directly and the elements switch off, you and the van are still cold but the sensors toasty and takes forever to cool before switching the fire back on!!
A few common bad places to find the switch are in the side of the wardrobe above the fire or in a bed box where blown air pipes run, or perhaps even behind where the TV sits so the heat from the back of the TV or it’s transformer warms it up!
Due to this and particularly overnight, it's become something of an urban myth to set it at 500w or 1000w, this or that number on the dial and fan speed setting. In truth what's happening is the available heat is not capable of reaching the set temperature so never switches off, it's a useful work around but not how it should work.
The real solution is to fit a ‘remote’ temperature sensor and attach it to the gas fires sensor, if a remote is already fitted, it to will usually react better if moved to this location.

Setting the fan on manual speed means the fan runs at this speed regardless of the amount of heat being produced, I would suggest manual fan is only for use without heat for cooling in summer, if infact it has a use?!
Setting the fan to ‘A’utomatic allows the heat produced to control the fan speed ‘up’ to the speed set on the dial, you can then, keep this set maximum low and therefore quiet, overnight perhaps?
Automatic means the fan will run slowly initially and speed up as the air passing through gets warmer, doing it this way allows heat and fan to be switched on together and doing away with waiting xx minutes as often suggested.
I would suggest as a start and during the day, the wattage selected is as high as the hook up allows and then fan speed set to maximum on Automatic.
This provides the maximum heat if required and the fans speed will respond to change in temperature, ie, fast when heat cycle is on and slow when heat is off.
After that you can fine tune to suit your own needs

Other heating problems concern the control board, the elements are switched on and off by relays and the contacts burn out, particularly the two 1kw relays. If this happens you may think you have it set to 2kw but only one element is working, finally perhaps leaving you with just 500w working when both 2kw and1kw settings no longer work.
(Note, relays will still be heard to ‘click’ but unless you have heat, their not working)
The 12v for control also comes from this board and the transformer sometimes packs up, apart from no heat, you will lose the green light in the switch if this happens
Also if no heat is forth coming, there are two safety thermostats which switch the power to the elements off if things to hot. The lower one set at 125C will automatically reset after cooling, the higher 175C stat will hold itself off until power is removed, you must then switch off the mains supply to the heater and then it will reset automatically after a few minutes when power can be restored.
The lower 125C stat can fail when hot but well before it’s set temperature, this will mimic a relay fault and the heating switch off before the set temperature on the dial is reached. However checking the stat for continuity when cold will show a perfect reading, only way to be sure is to change it.

Note; if either thermostat is faulty it won't be able to reset, if faulty it can sometimes show itself by the vans main RCD tripping, but not always.

Finally, the mains isolation ‘fused switch spur’ can loose it’s connection through the built in fuse, the fuse is not the problem but the fuse holders connections that seem to be the problem

The main control switch itself seems generally reliable but the odd one does fail, the fan control switch when set to ‘A’ should make a positive connection and not switch on and off at the merest touch.

The numbers on the dial represent roughly 4degs and 9 is 32degs or thereabouts, this in theory makes 6 or 7 'normal' but it's what feels comfortable that matters not the number.

Other problems not caused by the heater itself are long runs of un-insulated blown air pipe running outside under the floor, insulating this will improve matters considerable.
The kitchen cabinet is often fitted over a wheel arch, much larger than required holes for clearance over the arch are used, the resultant heavy draught coming from behind the fridge can be eliminated by simply sealing the gap on the fridge side of the centre
cupboard.
Any draughts coming from the front of the fridge should also be eliminated.
Fix bed models very often have large floor vents under the bed, these are only useful in storgage and are easily block with a towel while the vans in use,

It’s also known for blown air outlets to blow toward the fire and this will upset the temperature control, adjusting these to blow away or even blocking off completely can actually improve overall heating.

Everything installed and working as it should, there is no good reason why the electric heating should not work very well and keep an even temperature to suit your needs.

However, it must be remembered the van needs to be warmed through thoroughly, (not just the air), before the heating is turned down. While the vans cold it will constantly drag heat from the air and this in turn needs constant topping up or the van will always feel ‘draughty’. It's most useful then while particularly cold to use gas as well for the first couple of hours, also, if the heating is off during the day to turn it back on at the first sign of a chill.
Blimey, now that’s a reply!
 
Oct 3, 2013
890
90
18,935
Visit site
I have just turned on the Truman heater in our caravan to run on electric hook up as on site however it doesn't seem to be working, turned it on to gas and no problem?

Any ideas?
Gas always heats up heat exchanger quicker,electric takes a bit longer but eventually heats up after a short time.
 