Well done in getting it sorted.
First off the 18th edition IET requirements for electrical installations is not a legal document , they however can be used along with other documentation to show an installation was designed, installed and tested correctly, if an incident occurs .
The use of an RCD is recommended , but within the regulations they are permitted exceptions and in the case of a TN-C installation they not permitted see chapter 41. The sixteenth edition of the IEE installations regulations also didn't fully state that RCDs shall be fitted ,in fact in the early edition ( before all the amendments) it said they weren't to be relied on solely for protection against electric shock.The consumer unit provided usually had a split system with some MCBs protected by an RCD and some not ( usually lighting circuits were the outlets are deemed 'out of reach') in the Eighteenth edition ( possibly even in the seventeenth) , as the reliability of RCD's has be proved . the use of RCD's in lighting circuits has been added.
One point to note is that the test button should be pressed every three months to ensure it works. I come RCDs in caravans and motorhomes which fail the full test and only after several presses of the test button , do they pass. This is because they are a mechanical device and the parts, if not exercised , stick together. Some even fail the time limits