Reg this is the method I used to eventually find the leak myselfA gas installer I know told me a while ago that the best way to find a gas leak was to either mix up a solution of soapy (dish washing up liquid) and water or buy one of the kids bubble making toys. Get a small paintbrush and go over every joint with it. You'll soon see where the leak is, you'll get a big bubble. Of course it will not find any internal faults with appliances or regulators.
After my recent experience where (hopefully) they found the gas leak but with the damage done to the external vents it doesn't inspire me with confidence.
And it cost me 200 quid!
Caravan servicing in my opinion is nothing more than a cash cow!
Thanks for your advice and help. I now feel that the service has not been carried out correctly and will be contacting the service manager first thing Monday morningHi Dave,
Firstly, the regulator problem is not a design "fault" as such, it is a combination of dirty gas and leaching of plasticiser from the pigtail, the GOK regulator is a two stage reg, as opposed to the older cylinder type which are single stage.
The test pressure is quite clearly stated, and there is a special test unit which has to be used to test the system.
The test is:
Isolate the regulator at the test point(to save back pressure on the reg), make sure all the isolation taps are open to each appliance, connect test pump and pressurise to 150mB.
Leave for 5 minutes and note the reading (the stabilisation period), leave for a further 5 minutes and note the pressure.
The loss of pressure MUST NOT exceed 10mB over the test period.
The test backwards from the test point to the cylinder is, after releasing the 150mB pressure, remove the pressure pump and connect a manometer, open the cylinder valve and note pressure on manometer, should be 28mB for Butane, 37mB for Propane, close valve and wait 5 minutes, note any loss of pressure9 must not be more than a value in a set of tables, which I do not have here right now.
Reduce pressure to 20mB and test for 2 minutes, should not be any rise in pressure, if there is it is a faulty valve.
Hope this helps
The response by CORGI is normal, they are not a technical service, as such, they are simply the registration body.
the pressure of 150mB is not for boats?Hi Dave,
Firstly, the regulator problem is not a design "fault" as such, it is a combination of dirty gas and leaching of plasticiser from the pigtail, the GOK regulator is a two stage reg, as opposed to the older cylinder type which are single stage.
The test pressure is quite clearly stated, and there is a special test unit which has to be used to test the system.
The test is:
Isolate the regulator at the test point(to save back pressure on the reg), make sure all the isolation taps are open to each appliance, connect test pump and pressurise to 150mB.
Leave for 5 minutes and note the reading (the stabilisation period), leave for a further 5 minutes and note the pressure.
The loss of pressure MUST NOT exceed 10mB over the test period.
The test backwards from the test point to the cylinder is, after releasing the 150mB pressure, remove the pressure pump and connect a manometer, open the cylinder valve and note pressure on manometer, should be 28mB for Butane, 37mB for Propane, close valve and wait 5 minutes, note any loss of pressure9 must not be more than a value in a set of tables, which I do not have here right now.
Reduce pressure to 20mB and test for 2 minutes, should not be any rise in pressure, if there is it is a faulty valve.
Hope this helps
The response by CORGI is normal, they are not a technical service, as such, they are simply the registration body.
sorry ment is it for boats :0the pressure of 150mB is not for boats?
What gauge is used for the 150mB test?
Dawn
yes damian, thats the set up i have. so the test pressure used was correct at least.Ray, it sounds like you have two cylinder mounted regulators, probably attached to a changeover valve.
It has never been known to fit two bulkhead regulators.
In this case testing at 50mB is right as it comes under the BS3016 regulations and not the EN1949 regulations