I am not familiar with F&S mcb's however many MCB's are now interchangeable and I would advise going to a local electrical wholesaler or even DIY store/ Screwfix and taking the old one with you to see if it has the same fixings points. They normally fit onto a din rail in most applications and this is where there can be a slight difference in shape and size.
Some better quality makes are MEM, Merlin Gerin, MK, GE although may not be a suitable replacement for an F&S
It may also be worth checking that the mcb has failed and there is not a problem elsewhere, if you are confident with electricity then (with the power off) disconnect the load side of the mcb and then switch it on and see if there is any voltage using test lamps or a multimeter. (no load test to prove mcb)If it is ok then you will need to start looking elsewhere for a fault.
I am surprised that it is only a 6 amp mcb and has the sockets and heater on it.
Simple calc is watts divided by voltage= amps therefore if you have a 2000 watt electric heater with a 230 volt supply it is roughly 8amps which would be too much for a 6 amp mcb even before there is anything plugged into the sockets.
The issue may be you are drawing too much load between the heater and the sockets and the mcb is tripping, unplug anything plugged into the sockets and switch the heater off and see if there is power coming out of the mcb.