Having a regulator go faulty is not good, Stop using it and disconnect the gas bottle(s) and rather than debating it on a forum for your safety you should be either getting checked or replaced.
I presume by your reference of "like Propane" that suggests you are using Butane. One of the issues with Butane at temperatures around 0C is its vapour pressure is so low that just dropping below 0C could cause any gas vapour in the pipes to condense into its liquified state.
When the ambient temperature rises the liquified gas will evaporate, but this time its on the wrong side of the regulator and it could exceed the normal 30mBar pressure producing larger flames at burners.
Whilst its not good to allow this to happen, and there are risks from it, it will only last as long as it takes for liquified gas to evaporate and the pressure will drop back and allow the regulator to re admit 30mBar gas to the system.
If what I describe is happening, you must change your gas to Propane.