Dave , this is scary serious stuff.
How can this situation be possible in 2025?
We had loads of rewiring and a new Consumer Unit two years ago. Nothing wrong with the old CU but the latest ICE regs said we needed a metal cased CU with more individual connections.
Does the break in the N wire have to be from the external socket via my adaptor and EHU cable? The thought of being electrocuted have the caravan at home is shocking(sic).
Is it being suggested that the mains adaptor is dangerous and shouldnât be used??
Surely they wouldnât be allowed to be sold if it was so dangerous?
One confused dog heređ
How come it's possible in 2025? ; basically because the wiring regulations relating to earthing are different for a caravan site to a domestic property, if they are followed everything is safe, however plugging a van in to domestic mains is introducing parts of the regs that are not required for a house.
To explain; there are different ways of providing an earth to domestic property, but by far the common especially in new buildings is
TN-C-S: which stands for "Terre Neutre-Combiné-Séparé" (Earth, Neutral-Combined, Separate), In this system, the neutral and earth conductors are combined (TN-C) in the supply network but then separated (CS) into individual neutral and earth conductors at your house. The danger occurs as explained in the video, when there is a fault between the earth and neutral
outside of your property .
When a caravan or motorhome is plugged into house mains with TN-C-S earthing, it' s not adhering to the UK Electrical regulations, but most folk (as one would expect!) wont understand what the regs are let alone what earthing system their property has!
The adapters themselves are perfectly safe in the correct situation, but that won't be with a high proportion of UK houses. Getting some sense of reality, the frequency when this sort of fault occurs is rare, but considered a high enough risk that caravan and camping sites are forbidden from providing mains with TN-C-S earthing.