Dougie. In the electrical testing industry there are various industry standards we work to as laid out in the IEE guide book 3. If it is imposible to unplug an appliance due to an inaccessable plug and socket, microwave fridge etc then that can be put down as a departure from the regs and a limitation used i.e. for l to n insulation resistance test you would insert LIM in the result box,similer with the r1 + R2 test.There is no need to examine the wiring in its entirity by pulling out appliances fridges cookers etc,you only inspect what you can see.If there is any doubt about damaged to electronics then the IR tester should be set to 250v not 500v. You can`t limit ZS or RCD tests though.it is permisable to obtain the circuit r1+r2 test by calculation from ZE ZS especialy if the EIC is present.
Really the NCC should not get involved in the electrical side.The only Caravan centre I know who used to have NICEIC registration and a full time proffesional electrician was Lowdhams in Nottingham I don`t know if he is still there but they are not on the NIC register anymore.
Really the NCC should not get involved in the electrical side.The only Caravan centre I know who used to have NICEIC registration and a full time proffesional electrician was Lowdhams in Nottingham I don`t know if he is still there but they are not on the NIC register anymore.